Rob said:Possibly, but isn't the negative on the battery connected to the chassis?
Yes - I meant don't connect the case to the 240v neutral

Rob said:Possibly, but isn't the negative on the battery connected to the chassis?
Rob said:I think the reason why we came to the conclusion to connect neutral, negative and case is because the manual says to ground the case, and the negative terminal on the battery is ground on the car![]()
Justin_Elliott said:Forgot to ask - has anyone changed the power mode for their inverter?
According to the manual, the mode can be selected by changing the jumper settings (on PCB behind top cover).
Modes available:
Standard - 230V output voltage
Low Power - 208V <30W
Economic - 208V < 250W
Standby - 0V until load connected...
![]()
Crispin said:Ground and neutral not the same thing here. Normal house power yes, not her.
Best would be to ground the chassis to the truck and if you really want, a spike into the ground (soil). That would give the RCD a fighting chance to save your life.
I fully understand but this came straight from the manual and it clearly shows 240V neutral connected to the case:Justin_Elliott said:Yes - I meant don't connect the case to the 240v neutral![]()
For safe installation it is necessary to:
• connect the earth (PE) and neutral (N) of the
inverter output to the central ground;
• insert a RCCB (earth leakage) switch of 30mA in
the inverter output.
The earth wire offers protection only if
the inverter cabinet is connected to the
earth. Connect the inverter's earth terminal (at the right hand side of the AC
terminal block) to the hull or chassis.
What voltage are you getting between the Earth pin on the inverter socket and the Live and the Neutral? When I served my time with ICI as a Tiffy all of the sockets in the research laboratories (old 5amp & 15amp round pin style) were fed using center tapped transformers so we fed 115v to each of the Live and the Neutral. This was for safety in the same way that we use 110v on construction sites in this country, if you put an electric meter between each of the Live and Neutral and earth on a site transformer you will get around 55v as these also are center tapped to earth. Maybe the Inverter is using the same principle hence your 115v readingCrispin said:So,
L -> N : 230V AC - as expected
N - > +12V : 115V AC - not expected
N - > negative : 115V AC - not expected
L - > +12V : 115V AC - not expected
L - > negative : 115V AC - not expected
I'm going to suggest that what is being see is half the sinewave (115X2=...) but putting it on the scope, it is a full sinewave so not sure.
No idea. I can't see it being a good thing in this type of installation (if the inverter case was not connected to the chassis I could understand it)
Rob, connect an inspection light between your Live and chassis. If all is well, the RCD will trip and everything is ok. Worst case, it will not and catch fire which means in a real situation, you would have been killed by the fault so in actual fact, you owe me
edit:
There is also nothing between the inverter chassis and the negative supply. They appear to be isolated. The blue line that you have could serve as a path if there is a fault on your negative wire.
If you negative lead comes loose and the inverter is connected to the chassis the path will now exist between chassis -> inverter -> your blue wire -> negative.
This [strike:ndbjbmeq]could[/strike:ndbjbmeq] would lead to a fire as it would not be strong enough.
Crispin said:Proceed with caution![]()